Fault correction
The following table describes a selection of faults. Depending on the application, other causes may be responsible for the malfunction. Conspicuous control behavior is the result of incorrect parameterization of the servo drive.
With multi-axis systems such as the AX8000, malfunctions may have different causes.
Error
Cause
Motor standstill no starting
1
2
5
Motor runs
sluggishly
1
3
5
6
Noises when
starting up
3
5
6
11
Noises during
operation
1
3
5
6
11
High temperature at idling speed
4
7
8
9
High temperature under load
1
3
7
8
9
Uneven
running behavior
10
11
Grinding noises
12
Brake fault
13
14
Output stage fault
5
15
16
Feedback error
17
18
No
brake effect
5
6
Leakages
19
Number
Cause
Solution
1
Servo drive not enabled
Set ENABLE signal and enable servo drive
Motor overload
Check the load and if necessary reduce it, then restart and enable the servo drive. Set ENABLE signal
Mechanical blockage of the motor
Check mechanics and release blockage
Holding brake [+] not released
Check the control configuration of the holding brakes [+] and reconfigure if necessary
2
Phase interruption in the power supply or reversed motor phases
Check servo drive and supply cables and replace any defective cables
3
Phase interruption after power supply; switching on
Power cable or feedback cable with defective shield
Check earth connection and shielding
4
Short-circuit in the voltage supply cable for the holding brake [+]
Replace defective cable, measure and check cable after replacement
Output voltage of the servo drive too low
Check the settings in the configuration and read out the electronic type plate of the motor again
Defective holding brake [+]
Replace motor, then measure and check
5
Short circuit or earth leakage in the motor cable
Replace defective motor cable, then measure and check
6
Power connector not fitted correctly
Check the connectors on the power connector and on the motor
Interruption in the feedback or motor cable
Check cables for broken wire or crushing. Replace defective cables, then measure and check.
Number
Cause
Solution
7
Required holding torque too high
Check design or configuration and adjust if necessary
8
Inlet temperature too high
Lower and adjust the inlet temperature
No more cooling water available
Replenish cooling water and check regularly
9
Motor heat dissipation system not functioning
Clean the surface of the motors and the servo drive as well as the heat sinks and exhaust air slots. Check the installation depths of the servo drives and motors.
10
Power cable or feedback cable with defective or insufficient shielding
11
Servo drive gain set too high.
Reconfigure the parameters of the servo drive and adjust them if necessary
12
Contamination or foreign bodies inside the motor
Send in motor. The repair is carried out by the vendor.
Rotating parts chafing on the housing or motor components
Inspect chafing parts and readjust if necessary
Defective bearings; irreparable bearing damage
Number
Cause
Solution
13
Replace defective cable, then measure and check
14
Inadequate power supply of the holding brake [+]
15
Replace defective motor, then measure and check
16
Insufficient power supply
17
Interruption or crushing in the feedback cable
18
Feedback connector not fitted correctly
Check the position of the feedback connector
Loose fit of the feedback connector or no contact of the plug contacts with the power socket of the motor.
Check the connector assembly. Contact Beckhoff Service if necessary.
19
Cooling water pipes and/or water connections leaky or defective
Determine leakage
If necessary: Seal